Hi, this is my first post here so please be gentle with me!

I have a Saunier Duval Thema F23 E boiler and I am having serious problems with this to the point of having to turn my central heating off and only use the hot water (very cold flat though!)

About a year and a half ago an engineer came out commented that my pressure was low, attached a metal hose between two valves and did something with a screwdriver which made a lot of water enter the boiler and pushed the pressure up.

The problem I have now is when I turn the central heating on the pressure shoots right up to about 3.5 and the boiler makes a really loud screeching noise a bit like a kettle boiling and there is a loud hissing.

When I unscrew either end of the silver hose loads and loads of water rushses out of my boiler but this doesn't affect the pressure. Any attempt to turn the small screw on the bottom of the right hand valve makes no difference to the pressure inside the boiler.

What on earth is going on with my boiler and how can I get the pressure down? It is obviously far too high which I think is the cause of my problem. I think the boiler is constantly filling up possibly due to one of those valves on attached to the metal pipe being broken.

Can anyone help me please?

Thanks
 
If you cannot work it out then I would recommend you get a competent heating engineer.


It sounds as if the original fault is the expansion vessel but you may now have the filing valve left open.

Saunier Duval are one of the worst boilers and the company used to have one of the most unhelpful attitudes to the trade with premium rate telephone numbers to call for bad technical advice after listening to their music for five minutes @ 50p/min !

Tony
 
Put the screw slot at 90º to the fitting. If it is in line with the fitting; the water is on and will charge your system up to the max.
Keep an eye on your pressure and make a note of what happens when you use the system. Ideally it should be about 1 - 1.5 bar.
In this case it is should hopefully stabilise anywhere between the 1 and 2.7 bar mark. If the pressure doesn't keep dropping AND the noise stops you should be ok to leave it at that until the next service. Chances of you being that lucky are about 1 in 5 I would say.
You are more likely to end up with a leaking PRV which may need replacing and possibly a pressure vessel problem as well.
 