Hi all,
I've recently moved into a flat that has a Baxi 105 HE connected to a Sunvic 2259 TLX thermostat.
The stat seemed to be very laggy so I popped it open to check it's wiring and the resistor.
The resistor isn't wired up at all, there's just Twin & Earth with black appearing to be Live and red Switched.
The trouble the Earth is connected to the metal back plate and was initially giving strange readings. Sure enough when the boiler is powered on the entire back plate is 120VAC referenced to a nearby water pipe (and later checked with an earth contact in a socket.
There is also another Twin and Earth running to behind the stat which is completely disconnected (cut)
I was initially planning to use the L/SL and install a battery operated digital Stat but the fact theres an earth wire at 120V when the system is on is a bit concerning (centre tapped to the boiler?).
The landlord is actually a charity shop so I was hoping to avoid any unnecessary call outs but I may not have a choice.
I haven't installed a thermostat before but I know my way around circuits
Bit of a long shot, but has anyone seen anything like this before and have a suggestion on how to proceed? Or have an idea where the 120V is coming from? It disappears when the boiler is off - also, although it's black and red by the stat, it's blue and brown into the boiler so clearly connected elsewhere.
I've recently moved into a flat that has a Baxi 105 HE connected to a Sunvic 2259 TLX thermostat.
The stat seemed to be very laggy so I popped it open to check it's wiring and the resistor.
The resistor isn't wired up at all, there's just Twin & Earth with black appearing to be Live and red Switched.
The trouble the Earth is connected to the metal back plate and was initially giving strange readings. Sure enough when the boiler is powered on the entire back plate is 120VAC referenced to a nearby water pipe (and later checked with an earth contact in a socket.
There is also another Twin and Earth running to behind the stat which is completely disconnected (cut)
I was initially planning to use the L/SL and install a battery operated digital Stat but the fact theres an earth wire at 120V when the system is on is a bit concerning (centre tapped to the boiler?).
The landlord is actually a charity shop so I was hoping to avoid any unnecessary call outs but I may not have a choice.
I haven't installed a thermostat before but I know my way around circuits
Bit of a long shot, but has anyone seen anything like this before and have a suggestion on how to proceed? Or have an idea where the 120V is coming from? It disappears when the boiler is off - also, although it's black and red by the stat, it's blue and brown into the boiler so clearly connected elsewhere.