Total RCD Protection?

Joined
22 Apr 2008
Messages
9
Reaction score
0
Location
Essex
Country
United Kingdom
I've just returned from living in the south of Spain where all the circuits in the consumer units are protected by one isolator and one RCD. I think this is because all of the supplies are overhead and the supplier doesn't supply a earth. Each supply goes to a metal pylon or similar on your property and that itself is earthed as an electrode into the ground. I think (but not attall sure) that this is called a TT system in the UK? Does this type of total protection apply here in the UK if no earth is supplied or can a split load be installed, with some not on RCD protection? I ask because i found that in a small nuisance fault situation everything was disconnected losing the lights and defrosting the freezer if i was away from home.
 
Sponsored Links
It's not compliant with 7671, but you do see older installations with a 30ma RCD acting as a main switch. Should have 100ma time-delayed RCD as 'main switch' protecting lights and a 30ma RCD to protect sockets etc. Do you have a 30ma set up now you're back home?
 
You must have RCD protection on all circuits if it is TT. You can use a split CU if the "non-main-RCB" circuits are protected by RCBOs.
 
Sponsored Links
Depends on how good your earth electrode is, it all about disconnection times in the event of a fault. I've worked TT systems where there is no need for RCD protection under the 16th edition.
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top