my system has a tower motorised valve fitted to the central heating system. heating does not work in auto position, i have moved the lever to the fixed manual position and the heating works ok. i have changed the motor but no difference. any ideas??
you need to get the voltmeter out and start looking where there is power and where there is not.
Its like a big game of join the dots....
power from the time clock to the room stat to the motor on the valve to the boiler and the pump.
Try removing the timeclock and making a connection from the live to the CH on connection, will be a diagram on rear of timeclock to show you which one this is.
If system then works then is timeclock, if not then link out the room stat and try again....