Utility room Extractor

Joined
28 Oct 2005
Messages
2
Reaction score
0
Location
Oxfordshire
Country
United Kingdom
hi can someone tell me it this is ok, i'm planning to fit an extractor fan in our utility room I plan to run a spur to a FCU using 2.5 twin and earth cable then run a 1.5mm twin and earth cable from the FCU directly into the Extractor fan. Cheers is this safe and correct ??
 
Sponsored Links
Sounds reasonable as long as the spur is fed from a ring socket and not another spur (Unless you have radial sockets).
Also if you are burying the cable make sure it is in the correct zones.
 
1.0 to the fan - they have TINY terminals, and 1.5 may over-power them (in a non electrical sense!).

Remember a 3amp fuse in the FCU!
 
Sorry BJS Spark, wasn't to sure what you meant about the cables and the coreect zones. what i was intending to do was place in the civity between plasterboard and brick, is that ok ??, thanks for the other relpy Guys.
 