Vailaint 424 lockout over night

Joined
24 Nov 2026
Messages
4
Reaction score
0
Country
United Kingdom
Hello all,

I have a valiant 424 eco tech plus here and it’s seems to lock out over night when on standby with a fault code f.23, when reset, I get the fault code back with f83.

However, when demand requested from the programmer, the boiler will run all day without any issues whatsoever so ever, seems to me this only happens over night when frost protection is active.

I have also seen the below when I go into “live information” when the faults are present.
“S98, flow/return temperature sensor self-test”

Also, when firing up for the first ten mins I have a message showing s.46 concert protection. ‘Minimum load - loss of flame.
I have never seen the flame bat on the screen showing its max when firing.

There also seems to be a tap sign that is constantly on even when the boiler is on stand by and not firing.

If someone can please assist and also let me know if all these issues are related to each other.

It’s driving me mad.

Thanks.
 

Attachments

  • IMG_8490.jpeg
    IMG_8490.jpeg
    434.7 KB · Views: 20
  • IMG_8476.jpeg
    IMG_8476.jpeg
    509.4 KB · Views: 20
  • IMG_8475.jpeg
    IMG_8475.jpeg
    508.6 KB · Views: 19
Your F.23 then F.83 on reset points to water not getting through the boiler fast enough, and the S.46 loss of flame at minimum load fits that. It only happens overnight on frost protection, which is the clue. When the programmer calls, a zone valve opens and the water has somewhere to go. On a frost run at night the zone valves are usually shut, so unless there's a working automatic bypass, the boiler heats a small amount of water that can't get away and locks out. Does it cycle on and off quickly while it's running? Is there a bypass valve on the pipework near the boiler, and do any rads have no TRV on them?
 
Thanks for the response.
This now makes sense as I belive on frost run the valve doesn’t generally open up.
I have noticed all when demand called for in heating all the radiators heat up except the one in an ensuite upstairs and the other in the hall way which doesn’t have a Trv - I believe thist the by pass. It seems like the inlet pipe to that radiator gets warm and after hours a small bit of that side will only get like warm however, the pipe at the other end of the radiator (return) stays stone cold.

The ensuite radiator just stays cold even the inlet pipe-have does not seem to warm up.

Also I had tried “chimney sweep” on the boiler - the temperature seemed to reach over 100 degrees which I don’t think it’s normal.
 
I have now got the radiator in the hall way working - looks like the lockshield valve was closed.

Waiting for the temp to drop to see if it happens again.

Tried chimney sweep again and it rose to over 100 degrees - both hot water and heating was off at the programmer…. Or should they be switched on when operating “chimney sweep”?

(Strange it didn’t lock out at that temperature , I manually canceled it as it got too hot).

IMG_8562.png


Thanks
 
Running in chimney sweep without any valves open and the heat will have nowhere to go. As for frost stat kicking in, maybe wire a frost stat in to bring the motorised valve on, which will bring the pump on.
 