On a VCW242 there are two OH stats. The one on the heating flowpipe cuts the voltage to the gas operator if the primary temp exceeds 97C, so the boiler will lockout. The stat itself is self resetting. The other OH is a 110C Ranco stat with a phial in the MHEX. This cuts the live supply on the main PCB, hence no pump, fan etc.
If you were wondering, I've worked with & for Vaillant for too many years to mention...!
The one on the heating flowpipe cuts the voltage to the gas operator if the primary temp exceeds 97C, so the boiler will lockout. The stat itself is self resetting.
Well if its not the 242, then which Vaillant has the manual reset OH switch cunningly hidden inside a whitish plastic cover to hide it from Chris's view?
Yes the one you are thinking about is the VUW 242 Turbomax. These have a black fascia and green knobs. That OH is even harder to find on the system boiler version, they put a wiring centre in front of it!