• Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.

Vaillant 828e DHW problem

kam

Joined
12 Feb 2004
Messages
4
Reaction score
0
Country
United Kingdom
I have a Vaillant TurboMax Plus 828e Combi boiler that has a problem with DHW. I have replaced the diverter valve and cleaned up the heat exchanger but the DHW is not activated when I turn on the hot water tap, the water runs cold.

Could it be the Aqua sensor or something else?

I can use the warm start feature but only when I turn the hot water temp setting on the boiler all the way.

Any help appreciated.
 
if the green light doesn't flash when the tap is running it's a faulty aquasensor.
 
Actually, I did notice that the green light was not flashing. Thank you.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top