The valve is to balance the flow to the heating versus the hot water.

It makes little difference to the reheat time and can help the boiler to work more efficiently.

Tony
 
Sponsored Links
Just fitted VRC430f +VR65 to existing ecotec plus 428. Looking for answer to same problem as Tommcdonna and tried The831bunny answer to tweak d77 and d78. It worked ! Boiler does not start on full load if d77 adjusted down and modulates correctly at the d78 temp. Need to watch out though - even if d77 down to 5kW cannot get boiler to modulate well at 70degreesC, but works perfectly at 8kW and 75degreesC - constant modulation ! When heating is on with water, the boiler load reverts to d0 setting and full load for 1st minutes as mentioned already here. :p
 