Vaillant Ecotec S.07 code

Ok so here's a update.

CBF kindly popped over today and so far has fixed the problem. Even upgraded the pump to a 15-60.

Working like a charm.. Will monitor closely when we move in and over winter.

Oh, btw his van is exactly as per pics... Magical van :)
 
  • Thanks
Reactions: CBF
Just want to say many many thanks to Dan for all the assistance.

And CBF for sorting.

I now have 2 very reliable plumbers stored in my phone now
 
  • Thanks
Reactions: CBF
Glad it is sorted.

What was the problem in the end?

Was I right in the view that the last people to look at it were Gibbons?

Lol spot on mate.

So a few probs:

1) pump is too small for house
2) pump was filthy
3) other bits of cleaning around other local pipes
4) d0 reduced by 1
5) whole central heating system balanced
6) bypass valve was broken. No spring in it. But workin for the time being. May need to replace it at a later stage

Voila
 
2) pump was filthy

Voila

Do you mean the impeller was blocked with debris causing the poor circulation which we had identified?

Part of ( proper ) power flushing is to ensure the boiler waterways and pump impeller are clear.

It would seem that your expensive power flusher did not do this!

Tony
 