right.. before I answer your questions guys.... I left the boiler of for a bit... ate my tea.. went back to it and it fired.. turned it on and it fired up...
so... with the CH on.. i turned the hot tap on... got hot water.... turned it off.. burners went out..as did the green and yellow lights on the fascia.... pushed the servo arm down and held it down and voila... the CH reignited... looking closely at the servo it is utterly caked it this white powdery corrosion. Is it a case of giving it a good WD40 to loosen it or is it a new servo needed?
The component that pushes the servo valve up is called the water section. It's possible that this is holding up the servo valve so it'll need checking.
Don't use wd40. It's a mineral oil and will swell the seals and wreck them..
Good thing is, you've found you fault. You're now gonna need an engineer to fit you a ne water valve and servo valve. The unit may take a little setting up in order to make it work properly.
Get an engineer that knows these boilers well. There are a few good ones on this site, and get them to give the Boiler a good going over. It'll be well worth it's money.
Better still... Do as MrV suggests and get someone in. It could save you a lot of headaches. Specify the boiler you have and what needs doing, some engineers don't like these and therefore don't know much about them.