Hello.
I have constant air in my CH system.
System:
Open vented fully pumped system with combined F-E as per boiler IOM. Boiler is a non condensing Suprima 50.
I've tried everything i know or read about and have been chasing the work of the ******s who originally put in the system for the last 20 years.
Everything i try has failed.
Some observations:
* It's air, not hydrogen.
* The system is clean, with ample inhibitor.
* Air vents etc installed at the system high points don't solve the problem.
* Pump is on boiler feed side.
*I see no leaks.
* I don't see significant water changes in the head tank
I think air is being sucked in somewhere. Two main culprits would be the actuated valve glands, or, the piping which is buried in the ground floor slab.
Pump is new and my TRVs are good quality. (Doesn't eliminate them though).
I'm fed up with it so i think i might change to a pressurised system.
Reading on this site, this seems to be a last ditch solution.
I have thought about putting sealer in the water to stop any leaks under the slab if thats the issue but i dunno. My boiler is old so thats not really an issue but still, its a bodge fix.
Any thoughts?
If this is good solution, any pitfalls or can i just add a pressure guage and expansion tank and hey-ho?
It's either this, or start ripping up floor boards and just fully replumb the whole thing as it should have been dine when installed.
Conments appreciated
I have constant air in my CH system.
System:
Open vented fully pumped system with combined F-E as per boiler IOM. Boiler is a non condensing Suprima 50.
I've tried everything i know or read about and have been chasing the work of the ******s who originally put in the system for the last 20 years.
Everything i try has failed.
Some observations:
* It's air, not hydrogen.
* The system is clean, with ample inhibitor.
* Air vents etc installed at the system high points don't solve the problem.
* Pump is on boiler feed side.
*I see no leaks.
* I don't see significant water changes in the head tank
I think air is being sucked in somewhere. Two main culprits would be the actuated valve glands, or, the piping which is buried in the ground floor slab.
Pump is new and my TRVs are good quality. (Doesn't eliminate them though).
I'm fed up with it so i think i might change to a pressurised system.
Reading on this site, this seems to be a last ditch solution.
I have thought about putting sealer in the water to stop any leaks under the slab if thats the issue but i dunno. My boiler is old so thats not really an issue but still, its a bodge fix.
Any thoughts?
If this is good solution, any pitfalls or can i just add a pressure guage and expansion tank and hey-ho?
It's either this, or start ripping up floor boards and just fully replumb the whole thing as it should have been dine when installed.
Conments appreciated