Viessmann 100-1 WB1B 30kW Pressure Loss

Joined
16 Mar 2015
Messages
5
Reaction score
1
Country
United Kingdom
Good Morning,

I'm hoping anyone can shed any advice before I have to get a plumber in, but I want to try and know what could be going on beforehand as I am at a loss what could be going on. A bit of brief information first, I live in a dormer bungalow and the boiler is situated upstairs in the WC, there are 10 radiators downstairs (approx half of them are only small) & 4 radiators upstairs. The boiler dates back to around 2010/2011.

I've been having a problem with the boiler losing pressure, but this week this seems to have got much worse to the point I have been having to repressurise daily - sometimes twice, the needle will litterally go to the bottom pin. The boiler does still function though other than gargling a bit when it first starts up, all downstairs radiators have no air in them, the upstairs though before repressurising will lose some air but no water comes out, in the WC their is a towel rail which is a similar height to the boiler so I actually removed the bleed valve from that and could observe that on each ocassion I did this there was still a considerable amount of water in the radiator except for the top two rungs. Obviously as the water heats up water does then start coming out of the bleed valve if I check when the heating is/has been running.

This made me start wondering if it could be the expansion vessel, so I've checked the copper pressure relief pipe outside the property and this has always been bone dry. I'd been reading some people also suggested it could be the heat exchanger that could have a leak, and in this case water would exit through the condensate pipe, so a couple of nights ago I disconnected this and placed the pipe into a bucket, the following morning it was still empty, however I don't think I repressurised the system when doing this.

I'd also read that if you repressurise the system and then isolate the boiler flow & return and monitor for any pressure loss this would indicate whether the boiler may have a fault or if potentially there may be a leak with the central heating pipework. So last night I did this and this morning woke up to a puddle on the floor underneath the boiler with some pressure loss (perhaps 0.2 bar) - I checked the upstairs radiators and they were all still full of water. I wanted to make sure that the boiler hadn't been flooded out, so did remove the case just to visually check and luckily there wasn't a massive amount of water around, it does appear to be coming from around where the heat exchanger is though and exiting where the hot water supply pipe is (but not from the actual pipe itself).

Now I did also just check around the schrader valve on the vessel and quickly pressed it with a screwdriver, air did come out, but some black water too, so I don't think that is a good sign? Just really not sure what happens if an expansion vessel fails where the water goes if this is not coming out of the pipe outside?

I have now reversed the isolation on the flow and return pipework & observed a slight pressure loss on the gauge probably due to whatever has left the boiler overnight, and also sat the condensite pipe in a bucket again whilst the pressure is about 1.2 bar just to see if any water does come out whilst the boiler is powered off. The case is now back on the boiler and haven't done anything else with this.

I am not ruling out a potential leak on a central heating pipe somewhere though, as we have changed two radiators downstairs from Type 11 to Type 22 back in early November and achieved this by using some compression elbows rather than having to lift sections of the floor up, and everything did seem OK this past few weeks however. Although it is interesting that the radiators upstairs were all still this morning though after isolating the boiler flow/return pipes.

Would appreciate any input from anyone.

Thanks
 

Attachments

  • IMG_20221211_084337065.png
    IMG_20221211_084337065.png
    1.5 MB · Views: 19
  • IMG_20221211_084358976.jpg
    IMG_20221211_084358976.jpg
    233.6 KB · Views: 23
Last edited:
Sponsored Links
Sounds like you have more than one problem. Boiler leaked internally ,when isolated ,the pressure dropped further when isolation valves opened ,indicating a leak on the system side too.
When heating is in use for an hour ,what does pressure rise to ?
 
Sounds like you have more than one problem. Boiler leaked internally ,when isolated ,the pressure dropped further when isolation valves opened ,indicating a leak on the system side too.
When heating is in use for an hour ,what does pressure rise to ?

I am certainly not dismissing a potential system leak as obviously I know the pipework has been disturbed to two radiators, but the system has been pretty stable since they were changed early November, I've kept having to bleed the highest radiator upstairs, but never had to top up the system like I've had to this week.

Would it not be expected that the pressure would drop a little when removing the isolation from the flow/return if the boiler has lost some water to counteract this?

I've usually been topping up to 1.2 bar & the spindle usually settles at 1.8 bar when heating has been on for an hour. I've got my flow set to 50 degrees on my Nest thermostat.

Cheers
 
Last edited:
With boiler flow and return isolated ,boiler leaked and pressure dropped. When isolators opened ,pressure dropped even further ,that's indicative of pressure loss on the system.
It's not rocket science.
Your EV appears to be handling expansion.
PRV pipework isn't emitting water.
Nothing coming out the condensate pipe.
Leak from boiler a certainty ,pool of water seen.
And an INDICATION of pressure loss on the system ,not totally conclusive.
 
Sponsored Links
With boiler flow and return isolated ,boiler leaked and pressure dropped. When isolators opened ,pressure dropped even further ,that's indicative of pressure loss on the system.
It's not rocket science.
Your EV appears to be handling expansion.
PRV pipework isn't emitting water.
Nothing coming out the condensate pipe.
Leak from boiler a certainty ,pool of water seen.
And an INDICATION of pressure loss on the system ,not totally conclusive.
And should there be any moisture when releasing some air from the EV? I could tell it was a mixture of air and water as my fingers were wet.

Just confused when the boiler was isolated and a pool of water formed why did that happen as opposed to the other times?

As you say there is clearly pressure loss on the system, I just want to try and have an idea what maybe going on if there is something happening within the boiler on top of a system leak.

I think I'll have to reach out to the plumber and take it from there really.
 
Small amounts of water from EV is not uncommon, not good ,but it's working,and could do with attention.
Anyone's guess where water loss from boiler eminates from,could be a slight leak that previously evaporated by heat in boiler,who knows without being on site to investigate.
Engaging an engineer is definitely required.
 