Just noticed that simond has a Viessmann background. Therefore, here more details in case it helps. I´ve set HW temperature to 46 C, boiler cut-off to 68 C, increased the circulation pump to 85% and set the heat xurve to 1.3. Everything works perfectly when HW is not drawn, all temperatures are where they should be, the circulation pump speed increase has even reduced the number of heating cycles. When I draw HW, the boiler shuts off when it should, but the boiler temperature keeps creeping up for about 20 seconds. When it peaks above 105, the fault F2 and the red light appears. I have managed to get going the last few weeks by gradually lowering the boiler cut-off point. When the red light does not appear (peak temperature remains under 100 C), the voiler starts and stops at very short intervals as the boiler temperature goes up very quickly.
Hope this helps!
Hope this helps!