Good afternoon,
I am wondering if anyone can shed any light on what might be wrong with my boiler. Firstly it was in the house when I bought it a little of 12 months ago, I have not installed it / had installed myself.
The symptoms are:
DHW runs warm, briefly cold then stays hot, I think this is a secondary NTC problem but I can live with it.
CH runs from cold up to 51-53 degrees and then the flame cuts out, the temperature drops to 40 degrees and it fires again until 51-53 degrees. It has done this all afternoon. I am measuring the temp with a Bluetooth temperature probe. The probe is attached to the side of the heat exchanger by the CH flow pipe. The rads are not warming as the water doesn't seem to be getting hot enough?
So far I have carried out the following:
Bled the boiler by closing the return valve and using the filling loop and the PRV until I can't hear any more gurgling. Open the return valve
Remove the screw from the centre of the pump to check for freedom of movement of the spindle and to remove any air. The spindle rotates easily. The three-speed switch on the pump alters the light hum of the pump motor.
replaced the primary NTC with a new OEM NTC. The new one is 10.6 Kohms at room temp the old one is 9.6 Kohms at room temp.
Checked the High Temp cutout and it shows 1 ohm at room temp, can't test at 80 degrees because the boiler doesn't get that hot before shutting down. I have bridged the thermal cut out as well in case it was operating at a lower temp. The boiler stills shuts down at 51-53 degrees.
I can't find any air in any of the rads all the valves are open.
The pump remains on when the flame extinguishes and the light flashes green indicating demand?
I have cleaned the system with X800 Sentinel and flushed it through. I have also removed and hosed out two rads downstairs which only ever got lukewarm
This model of boiler doesn't seem to have a mechanical diverter valve as such.
It doesn't seem to be air lock, iso valves, thermistors or pump.
My next thoughts are PCB? Any other suggestions?
Thanks in advance and sorry for the lengthy post...
I am wondering if anyone can shed any light on what might be wrong with my boiler. Firstly it was in the house when I bought it a little of 12 months ago, I have not installed it / had installed myself.
The symptoms are:
DHW runs warm, briefly cold then stays hot, I think this is a secondary NTC problem but I can live with it.
CH runs from cold up to 51-53 degrees and then the flame cuts out, the temperature drops to 40 degrees and it fires again until 51-53 degrees. It has done this all afternoon. I am measuring the temp with a Bluetooth temperature probe. The probe is attached to the side of the heat exchanger by the CH flow pipe. The rads are not warming as the water doesn't seem to be getting hot enough?
So far I have carried out the following:
Bled the boiler by closing the return valve and using the filling loop and the PRV until I can't hear any more gurgling. Open the return valve
Remove the screw from the centre of the pump to check for freedom of movement of the spindle and to remove any air. The spindle rotates easily. The three-speed switch on the pump alters the light hum of the pump motor.
replaced the primary NTC with a new OEM NTC. The new one is 10.6 Kohms at room temp the old one is 9.6 Kohms at room temp.
Checked the High Temp cutout and it shows 1 ohm at room temp, can't test at 80 degrees because the boiler doesn't get that hot before shutting down. I have bridged the thermal cut out as well in case it was operating at a lower temp. The boiler stills shuts down at 51-53 degrees.
I can't find any air in any of the rads all the valves are open.
The pump remains on when the flame extinguishes and the light flashes green indicating demand?
I have cleaned the system with X800 Sentinel and flushed it through. I have also removed and hosed out two rads downstairs which only ever got lukewarm
This model of boiler doesn't seem to have a mechanical diverter valve as such.
It doesn't seem to be air lock, iso valves, thermistors or pump.
My next thoughts are PCB? Any other suggestions?
Thanks in advance and sorry for the lengthy post...