Okay, I am having a bad boiler day. My Boiler is a 3 year old Vokera Linea 35HE. It was fitted to a part existing system ( 3 rads) and was extended (6 rads). I live in the Edinburgh area so Limescale not a problem here. To recap what's happened and what I and the engineers have done:
1 Over the past few months my Vokera Linea 35HE has started running hot then cool/cold with the DHW demand. It has been steadily getting worse.
2 On Saturday, a Heating Engineer replaced the secondary DHW thermistor - the fault appeared to be fixed but it returned in the evening.
3 On Monday; a different engineer (same firm) cleaned muck from the condensate trap - but the fault returned again within the hour.
4 On Tuesday I tested the temperature difference at 40C DHW by turning off the hot tap at 40C and noted the resultant primary temperature displayed which was 60C. (Perhaps indicating not a blocked Heat Exchanger?)
5 On Tuesday evening; yet another engineer (same firm) phoned to say the problem was definately the Printed Circuit Board. I queried if it could be the primary thermistor or Heat Exchanger and he said no chance. I haven't asked him to come out yet as he didn't seem to be interested in what had happened so far or what the symtoms were.
6 Tuesday night, I drained down the system and flushed some clean water through it before re-pressurising adn bleeding rads....This seems to have exasperated the problem, the boiler now does not appear to fire (no flame symbol on the display) although it does heat the water a bit so it must be firing for a short time. It flashes fault code 12 when it is trying to heat then resorts to code 10 (no flame detected) and requests a reset. Occasionaly the final fault code is 52.
7 Wednesday, I replaced the primary NTC thermistor and tried again. Still no joy.
I am now not sure if I've created a new problem or not. The boiler has been re-started/ disconnected from mains/ hold reset button in for 10 seconds etc. I thought perhaps there was air in the pump but it is all automatically released so shouldn't be that.
Any thoughts anyone. DP are you still online?
GW
1 Over the past few months my Vokera Linea 35HE has started running hot then cool/cold with the DHW demand. It has been steadily getting worse.
2 On Saturday, a Heating Engineer replaced the secondary DHW thermistor - the fault appeared to be fixed but it returned in the evening.
3 On Monday; a different engineer (same firm) cleaned muck from the condensate trap - but the fault returned again within the hour.
4 On Tuesday I tested the temperature difference at 40C DHW by turning off the hot tap at 40C and noted the resultant primary temperature displayed which was 60C. (Perhaps indicating not a blocked Heat Exchanger?)
5 On Tuesday evening; yet another engineer (same firm) phoned to say the problem was definately the Printed Circuit Board. I queried if it could be the primary thermistor or Heat Exchanger and he said no chance. I haven't asked him to come out yet as he didn't seem to be interested in what had happened so far or what the symtoms were.
6 Tuesday night, I drained down the system and flushed some clean water through it before re-pressurising adn bleeding rads....This seems to have exasperated the problem, the boiler now does not appear to fire (no flame symbol on the display) although it does heat the water a bit so it must be firing for a short time. It flashes fault code 12 when it is trying to heat then resorts to code 10 (no flame detected) and requests a reset. Occasionaly the final fault code is 52.
7 Wednesday, I replaced the primary NTC thermistor and tried again. Still no joy.
I am now not sure if I've created a new problem or not. The boiler has been re-started/ disconnected from mains/ hold reset button in for 10 seconds etc. I thought perhaps there was air in the pump but it is all automatically released so shouldn't be that.
Any thoughts anyone. DP are you still online?