vokera Mynute 28 SE boiler

Joined
14 Oct 2009
Messages
1
Reaction score
0
Country
United Kingdom
We have a vokera Mynute 28 96 SE boiler and when the heating is switched on only the boiler makes a loud rattling sound. The pressure remains at a constant 1.5bar however when the pilot light comes on the pressure gauge starts to flicker and then when the pilot light switches off (after only a few mins) the boiler rattles and the pressure gauge stabilises.

When the water is switched on at the same time as the heating the boiler does not rattle.
boiler
 
When the water is switched on at the same time as the heating the boiler does not rattle.
boiler

Based on that I would take the view that the pump is working but there is a blockage in the heating circuit ( or all valves are turned off ).

Did this suddenly start or did it come about slowly?

Do you have one or two motor valves? If two what make?

Tony
 