That's exactly the point. It doesn't matter to 50160 what happens within a 10 minute period, as long as it averages out within the limits.
I obviously realise that. It's the 'statistically unlikely' statement you mentioned that I have been talking about - as I said, without knowledge of the distribution of voltages within a 10-min period, one simply cannot draw such a conclusion. As you will understand, I could very easily produce a 10-minute set of voltages (say every 10 seconds, or whatever) which had an average of 230V, but which would indicate that it was 'statistically very likely' that some individual measurements would be pretty extreme (way outside of the limits for 10-min averages).That's exactly the point. It doesn't matter to 50160 what happens within a 10 minute period, as long as it averages out within the limits.
...The characteristics vary in a manner which is random in time, with reference to any specific supply
terminal, and random in location, with reference to any given instant of time. Because of these variations, the values given in this standard for the characteristics can be expected to be exceeded on a small number of occasions. ... Some of the phenomena affecting the voltage are particularly unpredictable, which make it very difficult to give useful definite values for the corresponding characteristics.
That's what I thought - but that surely makes it a very confusing (basically just plain incorrect) 'factsheet', doesn't it? Headed 'UK Supply' it explicitly says that the limits changed from -6%/+10% to ±10% on 1st January 2003 !!Yes the UK permitted variation is still +10/-6% but I think the stated limits are to allow for EU harmonisation where some countries are +6/-10%
If a limit is stated, I suppose one can't really blame them. It's a bit like trying to argue about doing 32mph when there is a 30mph limit (not that the police would usually try that one, but it's not impossible)! If there is some higher figure at which 'the situation becomes dangerous and immediate rectification is needed, then customers should be made aware of that figure, shouldn't they?One of our biggest issues with all this is the automatic assumtion that anything above the upper limit is dangerous and needs immediate rectification.

Indeed it is!That 'factsheet' seems to be a mine of misinformation.
That was my understanding, although I really don't understand what we're waiting for. AFAIAA, most/all EU countries (e.g. UK) are currently working with limits which are within the ±10% range, so all of them would be compliant with ±10%, even if it were to change tomorrow. Are there any EU countries who have a limit >10% in one or both directions?It seems, from internet exploration, that the 23= +/- 10% is an EU long term goal but DECC hasn't yet announced taking it up yet.
who works for a DNO, IIRC not a million miles from Westie
What sort of equipment did you have in mind? I can think of very few items of equipment likely to be found in domestic settings which have the ability to increase current to compensate for reduced voltage (to maintain power). Nearly all domestic loads are 'passive', such that reduced voltage will result in reduced current - although that current will obvioulsy have to flow for longer to achieve a given amount of energy (e.g. to boil a kettle).... but lower voltage means a lot of equipment takes more current.
You mean, apart from just about every electronic item which these days is universally driven with a switched mode power supply. These effectively exhibit a negative impedance - an increase in voltage results in reduced current, and vice-versa.What sort of equipment did you have in mind? I can think of very few items of equipment likely to be found in domestic settings which have the ability to increase current to compensate for reduced voltage (to maintain power).... but lower voltage means a lot of equipment takes more current.
I should have written "... very few items of high-power equipment...". I suppose you may be right that all the switched-mode PSUs around may add up to a significant total, but I was (perhaps wrongly) not consdiering them as representing a large proportion of the load on a network.You mean, apart from just about every electronic item which these days is universally driven with a switched mode power supply.What sort of equipment did you have in mind? I can think of very few items of equipment likely to be found in domestic settings which have the ability to increase current to compensate for reduced voltage (to maintain power).
Probably nothing major - but I was thinking (as I said, perhaps wrongly) that these very 'apart-from' heat-generating appliances accounted for the lion's share of the load on the network. Does anyone know the answer?So apart from cookers, kettles, electric heaters, and immersion heaters - have I missed anything ?
Quite wise. Given that most of them are the sort of scumbags who are happy to see extra old people die during the winter so that they can get their useless vanity projects subsidised, they aren't likely to demonstrate much sense of responsibility for any other consequences of their behaviour.I won't be holding my breath waiting for the renewables lobby to acknowledge the cost of dealing with this as having anything to do with them![]()