Yeap back again this morning. But it was after I opened the hot tap the cold started doing it again
Well, I suppose time to put your plumbing skills to use again.
You could, as suggested above, supply the "balanced" cold from the mains PRV but may be advisable to remove this and then T it off the mains to supply the cold only, this PRV will then just supply the cold and the ICG PRV will supply the UVC.
Or, as you suggested, install a shock arrestor in the existing balanced cold, however the balanced cold is connected indirectly to a 18L arrestor... the HW cylinder EV, if the hammer is in the balanced cold then the rising pressure will just open the IGV NRV and the EV should then absorb the spike (theoretically anyhow), of course, if it does reach the observed 8bar then the ERV (expansion relief valve) which is set to 6bar should be feathering as well, you might see some signs of this in the tundish. If installing the arrestor in the balanced cold doesn't work, you could install it before the mains supply just before the ICG PRV. Its your choice but repiping from the mains via its own PRV migh be the easiest "solution".