water pressure gauge noise

Joined
21 Jun 2011
Messages
133
Reaction score
8
Country
United Kingdom
hi
LONG STORY SHORT
Had new heating system and oil feed Worcester Bosch greenstar heatslave boiler ( boiler installed outside back of house) in ireland
Problem is in the mornings when heating has not been preset to come on and i turn the tap on (either in kitchen or bathroom) the water pressure dial vibrates violently with a loud humming sound
Now if the heating is preset to come on say the next day the vibrating and humming dosent occur
Also after turning on the water for a while or turning the taps on and off for a while the vibrating and humming eventually stops
The water pressure has been set to 3 and sometimes it goes down to 2.5 after use
the dial in the boiler is at just over 2( whatever that is) and the other dials are as seen in the uploaded pics
If any of you guys or gals have any more questions to ask orcould give me some advice i would be very grateful

 
Sponsored Links
Sounds like you have very high water pressure in the area and perhaps a pressure reducing valve.

Fit an small expansion vessel to the cold main in the house set at about 2 bar should sort it out.
 