Sorry for being a newbie with little experience here. Next week, as soon as I've flushed my system to remove X400 I poured in the system last weekend, and refilling the system, I will then be rebalancing all the radiators in my house.

Today, while checking if my water pump needed venting, I noticed the pump was set quite high. It's a Grundfos Alpha2, and it was set on level 3. Does it need to be this high? My house is fairly small with 11 radiators. So I was thinking of dropping this to level 2 to save on the electric bills, or maybe even level 1!? Should I do this before balancing the radiators next week, or wait until after as it might affect the balancing?
 
Was your system restricted ? Someone may of lifted the pump speed to overcome the issue, start on 1 with the pump
 
Do you know which mode it is in? There are three modes, fixed speed, constant pressure and proportional pressure.
 
Was your system restricted ? Someone may of lifted the pump speed to overcome the issue, start on 1 with the pump
We've only lived in the house since 2018, so have no idea. The balancing in the house seems awful, at least 2 radiators are mostly stone cold. It's been like this since we moved in. So perhaps the previous owners increased the pump speed due to the poor system balance, it's certainly a possibility. So I think I will try the pump on Speed 1 to begin with when I rebalance the system.
 
The balancing in the house seems awful, at least 2 radiators are mostly stone cold. It's been like this since we moved in. So perhaps the previous owners increased the pump speed due to the poor system balance, it's certainly a possibility. So I think I will try the pump on Speed 1 to begin with when I rebalance the system.

Before attempting to balance them, start by ensuring they are bled. Another possibility is that they are cooler due to a restriction in the flow to them, either an airlock, or other debris in the pipes or the actual radiators.
 
We've only lived in the house since 2018, so have no idea. The balancing in the house seems awful, at least 2 radiators are mostly stone cold. It's been like this since we moved in. So perhaps the previous owners increased the pump speed due to the poor system balance, it's certainly a possibility. So I think I will try the pump on Speed 1 to begin with when I rebalance the system.
11 rads will probably require ~ 1m3/hr
speed 3 at 6.2M will give this flowrate at a 5.2M head, speed 2 (3.0M) 2.8M, forget speed 1 (1.0M)
Constant pressure CP 2 at 4.5M might be a good starting point and then just possibly either speed 2 above or Cp1 at 3M.
I have 10 rads that require 3.6M with all TRVs calling for full heat which my Wilo Yonos Pico supplies at a 4.7M PP (proportional pressure) setting.
 