Wiring extractor fan with timer - Does this order look right

Sorry to hijack this thread, but why must L and N be isolated on a fan, when it is deemed acceptable to isolate a whole circuit using a SP MCB?
 
Sponsored Links
Sorry to hijack this thread, but why must L and N be isolated on a fan, when it is deemed acceptable to isolate a whole circuit using a SP MCB?

Isolation devices should preferably be double pole. 537.2.2.5

A double pole switch, circuit breaker and plug top & socket outlet may be used to switch off the supply during mechanical maintenance. 537.3.2.1
 
Sponsored Links
Hi guys, Just to clarify my OP - though we seem to gone onto a different area now - I don't want to link the fan to the light (because the bathroom has a good window). I do plan to link to a lighting circuit. However, wouldn't it also be possible to link to a socket circuit if an FCU was used?
Thanks for all the replies.
Reg
 