Wiring for hive active heating

Joined
11 Apr 2022
Messages
3
Reaction score
0
Country
United Kingdom
Afternoon

I have just installed the hive combi boiler thermostat and wanted to see if I had done it right.

From Myson touch v2 to Hive.

Thank you in advance.
 

Attachments

  • FF380A7C-D20A-4F8D-B80F-C3563597A582.jpeg
    FF380A7C-D20A-4F8D-B80F-C3563597A582.jpeg
    190.2 KB · Views: 82
  • 1CD5A3CF-01F1-4AD2-8643-9867B3D377C6.jpeg
    1CD5A3CF-01F1-4AD2-8643-9867B3D377C6.jpeg
    165.3 KB · Views: 93
  • 8300871B-B48F-4F09-BA3D-F69823F87444.png
    8300871B-B48F-4F09-BA3D-F69823F87444.png
    365.3 KB · Views: 83
Sponsored Links
When there are two conductors in a clamp terminal a more reliable connection is made when there is one conductor each side of the screw.

upload_2022-4-12_8-28-56.png


This method keeps the clamping plate level with equal pressure on both conductors.

If both conductors are on the same side of the screw then the clamping plate can tilt pivoting on the conductor nearest the screw.
The conductor nearest the screw gets the majority of the pressure from the clamping plate while the conductor furthest from the screw has much less pressure from the clamping plate and hence a poor / unreliable connection is formed.
 
Sponsored Links
What do you think?
 

Attachments

  • 8DAF6930-2290-4642-A50B-5364E674356F.jpeg
    8DAF6930-2290-4642-A50B-5364E674356F.jpeg
    184.4 KB · Views: 71

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top