worcester bosch 240 combi RSF

Joined
28 Apr 2008
Messages
2
Reaction score
0
Location
Yorkshire
Country
United Kingdom
pressure gauge kept showing a reduction in pressure so i replaced the pressure relief valve still same problem so replaced diverter valve diaphram not sure if this has solved this problem yet .Other problem the DHW is not functioning properly the water doesn,t come though very hot .Burner lights up as it should when demand for CH and DHW good blue flame .CH works well nice and hot .When hot water tap is turned on burner ignites but water is luke warm the CH system also starts when turning on hot water tap .DHW does come a little warmer when rads are up to heat .When feeling the pipes that leave the water heat exchanger the pipes to central heating are hot but to the DHW is luke warm have I just answered the question is the water heat exchanger US appreciate any help thanks
 
Sponsored Links
Sounds more like the DV is stuck mid position. The ch flow should not get hot when only hot taps are running.
 
Thanks Dave for your quick reply, that explains why it would heat the rads up but once they have got to full temperature why wouldn't the domestic hot water reach full temperature? Can you shed any light?
 
Sponsored Links
Just replace the diverter valve and check the expansion vessel.
 