Hi, I have moved into a 2 bed flat built in the 90s and trying to figure out why I heating problems even though the central heating and boiler "works" something is not quite right. There is a separate issue of a communal extractor system always pulling air out of the bathroom which I will ask the neighbours about separately, here I ask about a particular heating situation discovered after balancing the radiators.
System & Balancing:
Despite prioritizing the lounge, the radiator surface struggles to get past 50°C. However, the boiler's service menu i14 (Return Sensor) reports 60°C.
Temperature Facts:
Thanks in advance for any advice!
System & Balancing:
- Worcester Greenstar 28 CDi Compact ErP in a 2-bed flat, installed in the kitchen.
- Pump: Mode 4 (Max Constant Pressure).
- Balancing: The lounge radiator is undersized for the large room, so I have opened the lockshield an extra full turn to maximize flow. All other radiators have TRVs/lockshields dialled back specifically to prevent them from stealing flow.
Despite prioritizing the lounge, the radiator surface struggles to get past 50°C. However, the boiler's service menu i14 (Return Sensor) reports 60°C.
Temperature Facts:
- Boiler i14 (Return): 60°C.
- Manual pipe reading: 45°C on the Return pipe at the filter. (Measured using a digital kitchen thermometer held firmly against the copper pipe).
- Lounge Radiator: 50°C (measured with a radiator fan sensor and the same digital kitchen thermometer)
- Outside Temp: 2°C–5°C.
Thanks in advance for any advice!