Just looking for a wee bit of direction on where to go with this.
Installed a new 4 kw gas fire. Gas supply comes into property in 22mm drops to 15mm for around 2m then the last 1100mm is in 8mm with 3 formed bends around the chimney breast and into fire.
Min working pressure at appiance is 17.05mb, however I am acheiving 16.5mb.
Suggestions have been to take form bends out of equation by fitting a pedestal and 8mm rod straight to fire, however customer wasnt keen on the ped protruding out the floor.
Any advice would be greatly appreciated thanks.