zone valve keeps going to auto

Joined
15 Dec 2007
Messages
4
Reaction score
0
Location
Yorkshire
Country
United Kingdom
my central heating works but only if before it comes on, i go upstairs to the zone valve, and set it to manual. This is the only valve i can find ( new house) and is only 2 port (1 input 1 output).
Every time the heating goes off and the timer comes back on, no heat in radiators, I check the valve and its gone back on its own to auto!

Any help or is the valve broke?
 
Sponsored Links
It should always fall back to auto position. sounds like new motor required
 
Maybe wired wrong, the motor need a permanent live to work
 
Sponsored Links
Wrong the motor needs a switched live through clock then cyl/room stat.
The microswitchwithin the valve needs a permenant live (if its used)
 