Are you sure you've read the OP correctly? I see no suggestion that joints between copper pipes have been replaced by plastic ones, only that a lot of the copper pipe has been replaced with plastic, using plastic joints.Ideally you would need to loop/link across all the the copper pipes where you have used plastic joints, using 10mm CSA earth cable.
Firstly, it is NOT earthing, it is bonding - required because the pipes are or were earthed and are extraneous-conductive-parts.I've replaced a lot of my plumbing in the house with plastic speedift pipe and connections... A lot of my earthing was attached to the copper piping, what do I use as alternative earthing now?
Nothing.What am I missing?Ideally you would need to loop/link across all the the copper pipes where you have used plastic joints, using 10mm CSA earth cable.
Thanks for confirming that I wasn't going mad! As for 'especiallys', I think I would also add the "10mm² CSA" bit. He surely wasn't talking about some sort of 'primary bonding in bits', made up of lots of 10mm² links across plastic interruptions??!!Nothing. Quite frankly - it's a very strange statement - especially the part about using a continuous length of cable.What am I missing?Ideally you would need to loop/link across all the the copper pipes where you have used plastic joints, using 10mm CSA earth cable.
... earth bonding ...
You wouldn't need an 'earth'. If water, gas, oil or any other service entered your house in metal pipe, there would be a requirement to bond that/those, from close to where they entered the premises to the Main Earthing Terminal near (or in) your consumer unit/fusebox, but that's all.So say its all plastic and copper pipe has been removed... How do I have an earth? what do I connect too, do I still need an earth?
its all plastic and copper pipe has been removed...So say its all plastic and copper pipe has been removed...
How do I have an earth? what do I connect too, do I still need an earth?
But we don't want to keep continuity.I don't think what I suggest was wrong, keeping continuity along all exposed conductive parts, hardly wrong, as I said could be argued against.
Oh that's plumbing.If we really wanted to pick at the bones, the real wrong thing is installing speed or compression fittings in position that may not be easily accessible if a leak occurred, which they often do in these type of fittings.
Continuity between exposed-c-ps is achieved via CPCs. Did you perhaps mean extraneous-c-ps? If you did, the pipes in question obviously wouldn't be that, if they were downstream of an insulating interruption. I'm confused.I don't think what I suggest was wrong, keeping continuity along all exposed conductive parts, hardly wrong,...
Those are plumbing, not electrical issues - but how are you suggesting one should join plastic pipes? One can't solder them!If we really wanted to pick at the bones, the real wrong thing is installing speed or compression fittings in position that may not be easily accessible if a leak occurred, which they often do in these type of fittings.