Glow Worm Combi 100e

Joined
21 Nov 2009
Messages
4
Reaction score
0
Location
Norwich
Country
United Kingdom
I replaced the automatic vent as it was seriously leaking, but since then I have had major problems. Presently after switching on the boiler and without any demand the boiler fires up, I presume over heats and locks out. I have disconnected all the pressure switches, pump, diverter switch gas valve and thermistors (one each at a time) and the lock out still occur, even without ignition.

Where do I go from here? Could I have damaged the pcb? Or best call an engineer.
 
Sponsored Links
I replaced the automatic vent as it was seriously leaking, but since then I have had major problems. Presently after switching on the boiler and without any demand the boiler fires up, I presume over heats and locks out. I have disconnected all the pressure switches, pump, diverter switch gas valve and thermistors (one each at a time) and the lock out still occur, even without ignition.

Where do I go from here? Could I have damaged the pcb? Or best call an engineer.

are you a gas safe registered engineer??
 
Only electrically disconnected. I know I am not qualified to do and have no intention of doing any gas work. I shall call the professionals for that.
 
Sponsored Links
usually on these the dhw flow switch microswitch is full of water shorting across and keeping a permanent demand on for hot water.
 
I replaced the automatic vent as it was seriously leaking, but since then I have had major problems. Presently after switching on the boiler and without any demand the boiler fires up, I presume over heats and locks out. I have disconnected all the pressure switches, pump, diverter switch gas valve and thermistors (one each at a time) and the lock out still occur, even without ignition.

Where do I go from here? Could I have damaged the pcb? Or best call an engineer.

are you a gas safe registered engineer??

As far as ollski's concerned, its ok.

Paul.
 
I had previously taken the dhw switch out, operated it and it seemed to work ok but the boiler still lit up with no obvious demand. I have just disconnected the inline connector and the fault dissapared!! I do recall that the hot water light used to dimly glow without demand, maybe this was prior indication that the switch was on its way out.

Ollski thank you very much for your advise. I shall con check the switch and get it replaced. Hopefully all will go well

You have saved me quite a bit on a pcb, which I thought was causing the problem
 
If it is definitely closed circuit it will be because the spindle is leaking which pushes the microswitch, you'll need to replace this brass housing cover too.
 
I actual;ly changed the brass cover and diaphram last year as it was leaking. It must have taken all this time to create a short cct within the switch.

Thanks again
 