Manufacturers don't make it easy to plan or re-use an electrical installation! They mostly seem to refer to the physical plate on the actual oven. This is so frustrating as you have to buy the oven and hob first and then design a new kitchen and wiring installation to go around them.
Some ovens give a hint that they can be connected to a shared outlet. One Hotpoint double-oven installation manual even shows splitting a 6mm² feed to the connection plate to two 4mm² cables to the hob and oven. This seems dangerous as the 4mm² cables are not sufficiently protected by a 40A CB (OK with a 32A CB though).
I am planning a small galley kitchen with electric hob and built-under single oven. I shall allow for a 32A supply to a 45A cooker point with the switched supply feeding the hob and an FCU for the oven (e.g. 2.3kW Hotpoint SN56EX). The 1.5mm² oven wiring mandates a maximum fuse of 16A.
The OSG seems to imply that ALL domestic cooking appliances should be supplied from a single 32A supply unless they total more than 15 kW. Only then should larger or dedicated supplies be considered. By having a 32A CB, the kettle socket is also reasonably protected.
I take the point that diversity ought not to be applied to a single component. Thus, if the largest component (oven or grill) draws a current greater than 10A, then the diversity calculation should be current of the largest component plus 30% of the full-load current in excess of this largest component. However, if the largest component draws less than 10A, then the OSG formula should apply.
The 2.3kW oven above draws 10A, so a single 13A supply could be used for two 2.3kW ovens.

Oh, and because I have a fused spur, I could plug both ovens into one double-gang socket!
It is not clear, maybe the diversity calculation should be only used when cooking appliances total more than 15 kW?