mcb size

Joined
20 Nov 2004
Messages
13
Reaction score
0
Country
United Kingdom
I have just fitted a 10.5 shower and the trip keeps on tripping the fuse is only a 30a so I know I prob need to replace could anyone please tell me the size fuse I need.

Thanks
_____________________
moderator

please note 20 your post has been split
 
Sponsored Links
10500w divided by 230 = 45.65amps

so you need a 50amp mcb and you will possibly have to change the exsisting wiring depending on what size cable goes to your shower and what route the cable takes.

i would suggest 10mm cable if you do not already have this
 
Although the 10.5kW is no doubt rated at 240V, I always put in a 45A myself. I take it you have rewirable fuses?
It also sounds like you have uprated an existing shower, you really should have 10mm/4mm Twin & Earth cable.

Steve
 