Memera 2000 40 amp b mcb
28 Aug 2023
I have a kiln, 7.6kw 230 volts.
I understand that 10mm twin core wire connecting to a new 40amp b mcb should work.
But googling some are saying that 6kw is the max for a memera 2000 mcb?
Any ideas. Should I be ok.
Exactly so why are people saying 6kw max on the mcb? Makes no sense right and I should be ok as 10mm wire and 40a mcb should be more than enough
Which all depends on the installation method of the cable ...
In the UK, the declared voltage and tolerance for an electricity supply is 230 volts -6%, +10%. This gives an allowed voltage range of 216.2 volts to 253.0 volts.
If the supply voltage is the maximum 253 then the kiln will be taking 8.36 kW ( 7.6 / 230 ) x 253 which is 33 Amp.
Running an MCB for prolonged periods at more than 75% of rated current can make the MCB hot enough to affect the operation of adjacent MCBs
Nowhere. Correct.
Some people say the world is flat. I saw something on the internet once which was wrong.
There is no maximum for such things.
Yes, literally more than enough as in too big and a waste - unless you have installed it in unfavourable surroundings.
The actual voltage in your house us most likely around 240v
(Test it and see)
Which for a resistive load like a kiln will put the current up.
So running wire from one room with the circuit breaker/mcb board into a garage behind the plasterboard for about 10 metres.
Looking at gettng one of two kilns. One is 7.5kw 230v the other reads 240v/29.13a/7kw.
I have a memera 2000 board.
If I'm right I concluded that a 40amp mcb type b with 10mm twin core cable would be ok?
Best wishes
Michael
Is there perhaps some confusion with the 6kA breaking capacity of the OPDs in domestic CUs?
Yes this is the thing. I worked it all out upgrading from 6 to 10mm and a 40amp type b mcb. Then someone said the mcb has 6kw max. These kilns are 7 to 7.5kw, so what would I do?