All those that I have worked on are not positive pressure in the way that the old boilers are. On the old boilers the fan is on the air intake and pressurises the whole casing. on condensing boilers the fan draws air from within the casing so the main casing is still negative pressure.
But there is one in the Buderus customer reports smelling gas, put a gas sensor on it and it hits the roof. On the Buderus there are two red rubberish seals through which a couple of electrical items pass I think one is the glow electrode the other the sense electrode. So what must be happening is that some of the unburned gas air mix escapes before it reaches the burner in the buderus example.There cannot be a leak of gas/air mixture because that would mean no flame and would be shut down within 5 seconds on flame failure.
The boilers mentioned with this fault had no insignificant leak of poc they had flames. In the case of the Ideals the burner box made of alloy is burned right through. The Gowworms are also trashed if left alone.There could be a leak of POC but even then as stated above a small leak would be recirculated.
Because the combustion conditions are so sensitive the flame would not burn if there was a very large recirculation as the O² would be insufficient.
Tony