I have a single socket behind a wardrobe with 3 lots of power cables coming into it. I want to put a new socket a metre away how do I connect these cables I want to blank the existing socket off |
|
| Back to top |
|
|
|
If you do not want to see this advert, click here to login or if you are new click here to join free. |
 |
plugwash

Joined: 28 Mar 2004 Posts: 7999 Location: United Kingdom Thanked: 132 times
|
Posted: Fri Jan 12, 2007 7:18 pm |
|
|
30A terminal block should be fine. |
|
| Back to top |
|
|
|
 |
mandsrees

Joined: 12 Jan 2007 Posts: 4 Location: West Glamorgan, United Kingdom
|
Posted: Fri Jan 12, 2007 7:53 pm |
|
|
| mandsrees wrote: | | I have a single socket behind a wardrobe with 3 lots of power cables coming into it. I want to put a new socket a metre away how do I connect these cables I want to blank the existing socket off |
plugwash
Do you mean that I put the 9 cables into the 30A terminal blocks |
|
| Back to top |
|
|
|
 |
plugwash

Joined: 28 Mar 2004 Posts: 7999 Location: United Kingdom Thanked: 132 times
|
Posted: Fri Jan 12, 2007 7:54 pm |
|
|
you need to connect all lives together, all neutrals together and all earths together (you should end up with 4 of each once you add the ones from your new socket)
a 3 segement long peice of 30A terminal block should handle this connection job easilly. |
|
| Back to top |
|
|
|
 |
RF Lighting

Joined: 31 Mar 2006 Posts: 16288 Location: Leeds, United Kingdom Thanked: 738 times
|
Posted: Fri Jan 12, 2007 7:56 pm |
|
|
3 lives into one terminal
3 neutrals into another terminal
3 earths twisted togeter at the end and connected to the earth terminal in the socket back box. |
|
| Back to top |
|
|
|
 |
Steve

Joined: 15 Apr 2005 Posts: 15756 Location: Yorkshire, United Kingdom Thanked: 211 times
|
Posted: Sat Jan 13, 2007 12:59 am |
|
|
| RF Lighting wrote: | 3 lives into one terminal
3 neutrals into another terminal
3 earths twisted togeter at the end and connected to the earth terminal in the socket back box. |
I thought this was frowned upon. |
|
| Back to top |
|
|
|
 |
RF Lighting

Joined: 31 Mar 2006 Posts: 16288 Location: Leeds, United Kingdom Thanked: 738 times
|
Posted: Sat Jan 13, 2007 1:56 am |
|
|
Normally yes, but the earth terminal in some back boxes are not very good so twisting will ensure earth continuity is maintained |
|
| Back to top |
|
|
|
 |
festa

Joined: 06 Feb 2006 Posts: 212 Location: Cheshire, United Kingdom
|
Posted: Sat Jan 13, 2007 9:56 am |
|
|
Wow yeah....i can remember when i was training and my tutor screamed not to ever twist wires together .....mind you he even blew his top when he found a wire stripper in my tool bag.
He would only ever let us strip wire with the tips of our wire cutters.
In the real world like RF says sometimes twisting is the only way to get those wires in safely. |
|
| Back to top |
|
|
|
|
|
 |
plugwash

Joined: 28 Mar 2004 Posts: 7999 Location: United Kingdom Thanked: 132 times
|
Posted: Sat Jan 13, 2007 3:19 pm |
|
|
maybe better to use another way in the terminal block to join the earths and then run a flylead to the box earth terminal (assuming the box is metal) |
|
| Back to top |
|
|
|
 |
ebee

Joined: 14 Aug 2005 Posts: 1624 Location: Lancashire, United Kingdom Thanked: 28 times
|
Posted: Sat Jan 13, 2007 4:08 pm |
|
|
Hang about,
first you should check it`s a ring and not a branched radial (tree).
Even then, if it is a ring with a spur on = 3 cables (9 wires) then you would end up with two spurs at one place on a ring, that`s a no no.
Check it`s a ring then extend the ring to your new socket.
I could tell you how to do that but I`d preffer you to contact a pro for safety.
Do not twist wires together, double them, and leave a blank plate over the site of the existing socket in order to indicate it`s position and therefore likely cable runs, also it allows inspection of the strip connector at a later date.
Last edited by ebee on Sat Jan 13, 2007 4:11 pm, edited 1 time in total |
|
| Back to top |
|
|
|
 |
plugwash

Joined: 28 Mar 2004 Posts: 7999 Location: United Kingdom Thanked: 132 times
|
Posted: Sat Jan 13, 2007 4:11 pm |
|
|
| ebee wrote: | | then you would end up with two spurs at one place on a ring, that`s a no no. |
and what reg would this be or are you just repeating hearsay? |
|
| Back to top |
|
|
|
 |
ebee

Joined: 14 Aug 2005 Posts: 1624 Location: Lancashire, United Kingdom Thanked: 28 times
|
Posted: Sat Jan 13, 2007 4:16 pm |
|
|
Ideally, all sockets on a newly installed ring would be on the ring itself, if spurring at any time, no more total spurs than sockets on ring, you may spur directly off the ring , or at point (socket say) or at the origin of the ring (the fuseway), only one spur at any one place (it`s a potential current draw problem if you use more), a point is either a single or a twin or a fused multiple.
The term spur I used above really means unfused spur, if you want multiple spurs off one place then it should be fused (ie 13Amp max = total of the spur itself) |
|
| Back to top |
|
|
|
 |
plugwash

Joined: 28 Mar 2004 Posts: 7999 Location: United Kingdom Thanked: 132 times
|
Posted: Sat Jan 13, 2007 4:20 pm |
|
|
| ebee wrote: | | only one spur at any one place |
i repeat my question can you give a reg that backs this up or are you just repeating hearsay?
also i don't see how two spurs from a place with no point is any worse than a spur from a point |
|
| Back to top |
|
|
|
 |
ebee

Joined: 14 Aug 2005 Posts: 1624 Location: Lancashire, United Kingdom Thanked: 28 times
|
Posted: Sat Jan 13, 2007 4:28 pm |
|
|
It`s not a reg in itself as such that specifically says "Only one spur at any place on a ring final" or similar, it is an agreed CONVENTIONAL CIRCUIT ARRANGEMENT that is derived from design consideration of the regs in their entirety and that part is in itself with refference to current draw and overheating of the cables/terminals.
Like in a similar fashion I don`t think there`s a reg that specfically says "Don`t open a live socket and stick your finger in it" yet the regs do conspire to make this forbidden (much as you`d expect really).
No think about what potentially could be the current draw at the place on a ring where two unfused spurs are connected. |
|
| Back to top |
|
|
|
 |
RF Lighting

Joined: 31 Mar 2006 Posts: 16288 Location: Leeds, United Kingdom Thanked: 738 times
|
Posted: Sat Jan 13, 2007 6:59 pm |
|
|
| ebee wrote: | | I don`t think there`s a reg that specfically says "Don`t open a live socket and stick your finger in it" |
Electricity at work act 1989
Regulation 14. |
|