Hot shower switch and cable
31 Mar 2008
Surrey
We have a 9.5kw Triton shower. I have run a 10mm cable from the CU to an isolation switch outside the bathroom (12 meters) and a 16mm cable from isolation switch to the shower (further 3 meters). Using shower for 10 minutes then no problem, but longer than that and the 10mm cable gets very hot and the isolation switch also gets very hot and starts to smell chemically. Can anyone suggest a course of action to remedy this? Or should just ignore, seems to still work ok?
P.S. yes, I did say 10mm and then 16mm. I ran out of cable!
The cable is running along the top of the skirting in a bit of trunking all the way.
Cheers,
Stuart
It might be too late if your cable or switch has already been damaged by heat :(
Indeed, you'll need to strip back the cable to bright copper and probably replace the switch
Thats 40amps + so all terminations must be very good or they will fail.
Stuart, is that a new install? Did you notify the work :?:
If the termination gets hot, the pvc sheath will melt and the heat will turn the copper black.
You'll never get a good connection on the copper so you need to cut it back.
And then having done that and reconnected you should do an R1+R2 test, and insulation resistance, to confirm that all is well.
And compare the test results with the ones that you got when you tested and certified the original install.............
I guess you did notify the work as well??
- Works in a special location (bathroom)
- Was it a new circuit?
Thanks everyone.
I took the switch off and found that the supply blue neutral cable had melted at the end and the copper had gone off color. So I stripped it back and replaced the switch (which had also melted slightly around the neutral terminal). Its now fine and not getting hot at all.
I dont know what you mean by notify. Notify who?
Cheers,
Stu
Surely your work involved replacing the cable with the same spec. and same route as the old one which suffered rodent or impact damage. In which case you don't need to notify it :D