You can't loop the earthing conductor in and out of the MET because only the cable between the MET and the means of earthing is the earthing conductor.
What about the bit of cable between the CU and MET?
And where are my bonding conductors earthed to???
You have the following connected directly to the earth terminal in your cutout.
A) Main earth conductor from the CU.
B) Main bonding conductor #1.
C) Main bonding conductor #2.
Why? One could speculate about an idiot having been allowed unsupervised use of a screwdriver, but that wouldn't change anything.
What to do?
B & C should be removed from the cutout. You can either open it up, or just cut them off. The former is preferable - it's neater and you can check that the connection is OK.
A can stay if the earth bar in your CU can accommodate B & C, or it can be removed from the CU and connected to a new external MET to which you connect B & C and a new "A".
possibly a dim question, but why do your earthing and bonding go to a meter?
If that were the case, is it not possible to disconnect at the gas/water and test Ze at the CU?
is a photo possible of the meter in question?
BAS just to be clear, you still need a connection from the CU to the external MET The last part of your reply could be read disconnect A from the the CU (but the other end still connected to the cut out) and just connect to the external MET. You would then have no link from the CU to the main earth.
A) Main earth conductor from the CU..