I have been playing with the bypass (low loss header?) on my dual boiler installation. The manual states a temperature differential across the boiler between 8°C and 20°C. The manual quotes efficiencies only for 20°C differential.
I think I've cracked it (the set up that is, not the heat exchanger).
I want to check that I haven't got things wrong:
First, I balanced the radiators for a 20°C drop with the radiator pump (Dunfoss 15/60) adjusted down to middle speed.
While the system is warming up on full power, I set the bypass valve so the temperature rise across the boiler is nearly 20°C - hopefully suggesting the bypass is adequate but not excessive. I take it that it is vital the temperature rise across either boiler does not exceed 20°C.
With the system up to temperature and the boilers and their pumps modulated down close to minimum, both the return temperature from the radiators and to the boilers match and are nearly 20°C below the matching feed temperature from the boilers and to the radiators - suggesting the flow through the radiators and boilers are similar.
The feed temperatures are 70°C (so hot water reaches 60°C) and the return temperatures are about 50°C (so there is reasonable condensation).