So that's £50 down the drain.I have fitted a new actuator and we can now rule that out as the boiler continues on with both thermostats turned down.
I'd forgotten that you replaced the complete valve. Did you put it in the same way round as the old one? Port A (marked on the side of the brass part) should go to the rads; Port B to the HW cylinderI am pretty certain the valve is not sticking - and in any case it is only a week old.
Of course; I should have remembered that.When in the fault condition with both stats turned down the manu/auto lever is loose. This is because the motor had previously been at the CH position and is still receiving power since turning the stats down - so is still in that position.
That's wrong!In the fault condition there is 240v on both grey and white (and orange).
Do you mean the white is 0V or the wire from the room stat is 0V?I disconnected the room stat feed where it meets the white and it is 0v, so the 240v is feeding out on the white from the actuator - obviously derived somehow from the grey wire.
The only way 240V can get from the grey to the white is via R2 (see the CH Satisfied diagram). This is normally a high value resistance, chosen to make sure 240V cannot get onto the orange and thus start the boiler.
That's as expectedIf I disconnect the grey wire at this point the motor returns with the spring to its rest position and the orange and white drop to 0v and stay there after I have reconnected the grey.
That's a possibility, but first remove the programmer from its back plate and check the connections are tight and no loose strands.While checking the problem with the new actuator I have observed a slight change in symptoms. I can now turn the heating off if I do it at the programmer, but if I try this by turning the room stat down it has no such effect - the boiler runs on. I noticed that if I twist the programmer slightly that the HW light comes on. I am now wondering if my problem is the programmer. Could the programmer be causing these symptoms due to a flaky connection (perhaps leaking the NOT HW signal onto the CH signal).