With a Continuity tester on the Ohms setting, test between each metal pipe
that enters the bathroom (Extraneous conductive parts) and the circuit
protective conductor (cpc/earth) of each electrical circuit in the bathroom.
If the reading is less than 1667ohms and all circuits are protected
by 30mA RCD’s then no Supplementary Bonding is required.
If any of the above requirements cannot be met, Supplementary Bonding
must be installed.
A bit of a wild statement - what if he does the test that you suggest and gets a reading of infinity - i.e. no continuity at all........does he supplemetry bond whatever the metalwork is and introduce a hazard that wasn't there in the first place??
Although 701.415.2(v) does, indeed, state that RCD protection is also needed in order to allow supplementary bonding to be omitted,I'm not entirely sure that I really understand the thinking behind that. I'm certainly not denying that RCD protection is a good idea for a bathroom, but I'm not sure why its absence should cause one to have to locally bond e-p-cs which are already (as required by 701.415.2(vi) effectively bonded together. Perhaps I'm missing something.Kind Regards, John
Maybe you're missing the fact that without RCD protection the disconnection time under earth fault conditions will be a lot higher (i.e. within 0.4 sec as opposed to 0.04 sec), so the rise in difference in potential between an 'exposed conductive part' (the 'fault') and other metal parts could be a lot higher due to the prolonged fault condition.
Supplementary bonding will therefore help reduce the difference in potential that may occur.
With an RCD protecting the circuit, and Main Bonding in place, it is not deemed necessary.
That's my take on it, anyway.