It will cost a whole lot more than that if you're not registered under one of the appropriate schemes.
Too f**ing right it does !
In my area, it's £150 for electrical works
IF you can provide them with the right test results. Since few DIYer will have the equipment for that, it then becomes about £225.
4) would anyone regard changing an MCB for an RCBO on any circuit as altering the characteristics of that circuit?
5) would anyone regard changing an MCB for an RCBO as re-designing the related final circuit?
No and No
Look at it this way - before you had an MCB, almost certainly type B, and of a specific current rating.
Afterwards, you still have an MCB, type B, and of the same current rating.
So from the POV of circuit protection, nothing has changed.
You have ADDED RCD protection to the circuit, but I cannot see any way in which that could adversely affect anything - other than nuisance tripping if there is any leakage current.
So I'd consider that provided the type and current rating are the same, then there is no way that swapping an MCB to an MCB+RCD (ie RCBO) could be construed as altering the protection characteristics or re-designing the circuit.
In fact I did consider doing just that - swapping out all the MCBs for MCBOs in the existing board. But in the end I decided it would have been too tight, and I wanted to add spare ways anyway. So I came to an arrangement with a friendly spark to do it.
I can see some logic why changing an MCB or swapping one for an RCBO would be allowed but changing the whole CU is not. The difference is in having to disconnect the main supply upstream of the main switch. Since many (most ?) installations don't have an isolator between meter and CU, some people would be tempted to do it with the tails live.
In fact, many years ago I know someone who was renovating an old house - and he moved the meter. Dropped the supply cable out, taped up the live core while he was ripping the house to bits, and then put it back together again afterwards.
Back then I didn't know enough to tell him to leave well alone.
Supplementary question ...
If swapping out breakers (whether like-for-like or MCB to RCBO), is it considered acceptable or not to use a different make of breaker ? I can't see any logical reason not to when they are of the same design - ie they fit just the same as the original make.