Does parallel really give you the same head? Can anyone show me how this works mathematically
do you get S53 when set to 26kw though?
I take it the pumps are in series?
that gives you more head same flow rate
in parallel will give you same head ,more flow rate
you need to have adequate head and flow-rate, just because you have two pumps it doesn't mean that you have the correct flow-rate andhead
your system is large for a domestic application it needs a better design spec
The boiler is shutting down because it is protecting itself from thermal shock
do you have a differential bypass fitted before the zone valves?
Matt
Yes, I have an autobypass fitted before the zone valves. This doesnt kick in on a cold system (i.e. it's not always bypassing, though Tony suggested this could be a possible workaround for this problem).
Even if you cannot work out a controller to alter the d0 dynamically as required then you could still create a simple relay based logic to actuate motor valves to provide bypasses when required to fool the boiler into thinking everything is normal.
In fact it could all be housed in a Tupperware box and have digital displays on the front!
Tony
What is getting me is how when the system is cold changing to 18kw stops the s.53 that comes after 20 seconds. As we know these boilers dont take into account during the first 50 seconds the value of d.0 and just fire at around 70% of max rating. Havent read the full thread but has it always been like this since install or have you inheriated the system.
Because Ignoring the valve of d0 or not has no impact on why it is shutting down with a S53 error
It's doing it to protect the heat exchanger from thermal shock
Matt