That's obviously true, but I still think that a PF of 0.8 would probably be unnecessarily pessimistic as a 'rule of thumb' to use for all circuits in a domestic installation, don't you?Anything with a ballast, an induction motor or a transformer will have a power factor of less than 1 ...
You're right - I wasn't thinking straightNo, as long as the cable rating is bigger than the over current protection, if you want to make your over current protection larger then you'll end up in a pickle.To use such a factor would essentially mean de-rating cable CCCs by 20% - which would mean, for example, that a 2.5mm² ring final (or 20A radial) would be non-compliant if any of the cable were not 'clipped direct', and that a 4mm² 32A radial would be non-compliant with any installation method.