Part 2 may have separate entries but the actual definitions are not dissimilar.
For incoming supplies the DNO will have used 16mm² for 100A supplies, so yes but if you calculate it will be less.
Also, should you have a 60A fuse then 10mm² is all that would be required regardless of that actually fitted.
No. I was replying to Daftpunk who had stated that 16mm² was required for PME.Agreed, and I only mentioned it because you, in turn, had mentioned it as an alternative to calculaion.I don't understand why anyone would want to use 54.7 - it is merely a cover-all figure ...
Yes, true - or quite.It's people (including a good few electricians), not Table 54.7, that have "the magic 16mm²" in their heads.
... but you said it was primarily for CPCs so could be 1mm².I suppose I shouldn't second guess the behaviour of DNOs, but I was assuming that 'S' (for incoming supply) would not normally be less than 16mm² - in which case the minimum CSA for an earthing conductor would, per 54.7, be 16mm² for any incoming cable size up to 35mm².