New Voltage and Socket Tester
28 Jul 2012
Surrey
Just a quick one for the regulars; just picked up my first proper voltage tester along with a Kewtech LoopCheck 107 socket tester and a DiLog socket break out.
I do wonder though, how many people buy socket testers with a built in loop test feature and plug it into a 25M/30M extension lead and think something is wrong when it says check loop impedance. The same goes for TT earthing systems.
Regards: Elliott.
Since like I am sure most electricians I have a proper loop tester, I have never bought the EZ150 plug in tester, however I have looked at the spec, and the first light is 1.7Ω there are from memory 4 LED's with two colours so there are 8 levels, so I would have expected the instructions to say what the 6 levels mean? However with a standard ring final the pass mark is below 1.7Ω so even if it says all is OK it may not be.
The one you show has just two 1.8Ω and 92Ω and although 200Ω is considered as a pass I suppose it is unlikely with water and gas bonded that you would ever get a reading below 92Ω with a TT or 1.8Ω with a TN if the system is OK.
There are a good tool to tell allied trades when it is safe to use the power provided, they are not an electricians tool, in some ways two limits of 1.8 and 92Ω is better then 1.7, 5, 10, 100, 200, 500Ω given with the EZ150 as how do you explain what they all means? It says power consumption 2.5W for the EZ150 which is about 10 mA and the Kewtech states 7 mA line to earth, so should not normally trip a RCD, however they both could push the leakage over the 15 mA minimum and cause the RCD to trip, there should be a warning in the instructions.
What does a loop impedance meter do to measure / calculate the loop resistance. ?
I am sure it applies a known load to the supply and measures the voltage drop that is caused by that load. Short duration, maybe only one or two cycles, to prevent the load in the meter getting hot.
So would using a 3 kW kettle as a load, an accurate RMS volt meter and the ability to apply Ohm's law give a good indication of the loop impedance ?
Likely yes, it would depend on how steady the supply voltage is, from generator with the only item being put on the circuit being the kettle it would be accurate, but with other items being put on and off load at the same time it would mess up your readings, measure two consecutive cycles and the chances of a load being put on or removed at the same time is reduced, and with any loop tester, do it three times and you will get three slightly different readings.
You may remember I wrote some software to use the loop impedance (line - neutral) to work out volt drop, in theory it works, however in practice it was found the loop impedance meter was not accurate enough to prove that the volt drop had been exceeded until it reached well over the permitted levels, measure 0.96Ω instead of 0.94Ω and that's 0.4 volt drop out and only got 11.5 volts to start with. At 1.36Ω with a ring final line - neutral your looking at 19.2 volt drop. Of course the loop impedance we normally quote is line - earth not line - neutral however we should be testing both, however line - neutral is normally expressed as prospective short circuit current, so should be over 244 amp to ensure volt drop of 11.5 volt is not exceeded on a 26 amp average circuit (20 amp centre and 12 amp even spread so 32 amp ring is calculated as being 26 amp for volt drop).
So 10 amp kettle should not cause the voltage to drop more than 4.5 volts if the ring final does not exceed the recommended 106 meters, so 4.5 volt = 0.94Ω approx loop impedance which is the limit for a ring final line - neutral to ensure with 26 amp it does not exceed 11.5 volt.
So a simple energy meter does not give and decimal point, but if when you switch on kettle it does not fall move than 5 volt then the ring would likely pass, if below 4 volt it would pass with flying colours, above 5 volt is a fail. So 6 volt would be 1.14Ω well over the 0.94Ω limit.
If you have no RCD then 8.3 volt = 1.44 with a 10 amp kettle. However the dangers involved measuring with a 10 amp load line - earth means we should not really do this test, if the earth was faulty we could be raising bonded metalwork around the house to 230 volt.