As I don't have a copy of the 18th - and the only draft document I can find does not say what I thought it did, would someone please be kind enough to post the actual final wording of 544.1.2?
actually made it
THE DPC showed no change relative to 17th. However, the April 2018 'final draft' showed the following changes, which are exactly reflected in the published version (green is added, red is removed - as compared with 17th):Thanks. I have just read similar elsewhere. I thought it was going to acknowledge at last that the consumer's side of an insulating section did not require bonding.
544.1.2 The main protective bonding connection to any extraneous-conductive-part such as gas, water or other metallic pipework or service shall be made as near as practicable to the point of entry of thatservicepart into the premises. Where there is a meter, isolation point or unionan insulating section or insert at that point, or there is a meter, the connection shall be made to the consumer’s hard metal pipework and before any branch pipework. Where practicable the connection shall be made within 600 mm of the meter outlet union or at the point of entry to the building if the meter is external.
See what I posted a few moments ago, whilst the rest of you were posting messages.Ok. Perhaps someone can confirm that is what has actually made it into the BBB.
Surely that means something which isolates the supply of whatever is in the pipe?it still talks about bonding after an 'isolation point' - which, if that means the same as an 'insulating section', clearly cannot be an extraneous-c-p!
Oh, maybe - I was thinking of 'electrical isolation'.I take isolation point to be the tap.