In a Schneider CU, yes.Double pole Schneider. Can this be used as the incomer to save space in he CU?
I suppose it all depends upon what you would regard as being a "useful level of discrimination" but, in terms of the sort of modest overloads the OP is considering/contemplating, I personally wouldn't say that it would necessarily be a 'useless' amount of discrimination.Never mind that, have you checked the curves of a 100A fuse and a 100A MCB to make sure there's a useful level of discrimination between the two? The answer will be a resounding no.
You seem to be ignoring the time factor. To blow a 100A service fuse you would have to have loads totally considerably more than 100A 'all being on simultaneously' for an appreciable period of time, which is exceedingly unlikely with any 'ordinary domestic loads' (and most 'not-ordinary' ones, too!). It should take half an hour or more for 200A worth of load ('all on, all the time') to blow a 100A fuse.The loads could be approaching the limit if all are on at the same time, not go over. I know about diversity, etc, which says you can put on larger loads as the probability of them all being on simultaneously is low. Best to be sure and put in a 100A mcb than can be user reset.
Primarily to protect against a (L-N or L-E) fault, if the fault is upstream of the CU or if the installation's protective devices doesn't clear it - and that fault current will potentially be many hundreds of amps. In a TN-C-S installation, even if the Ze is the 'maximum' of 0.35Ω, a fault near the origin of the installation would result in a current of almost 600A; if the Ze were, say, 0.15Ω (not unusual for TN-C-S), then a similar fault would result in a current of over 1,500A.If that's the case, wtf use is a 100A fuse? lol
The way we label fuses is fine for those who understand what the labelling means. A 32A MCB will typically allow about 46A flow for around an hour before tripping - do you think that we "might as well label it 46A"?Might as well label it 200A
Even a 100A MCB will allow 145A to flow for about an hour without tripping. Anyone contemplating using a current which averaged over 145A for at least an hour would presumably be doing something not intended to be done in domestic premises (and would certainly need DNO permission to do whatever they were doing).I am aware that service fuses take a time to blow, that is why the 100A mcb is in contention.
I agree. It would only go over 100A in some sort of fault condition.Even a 100A MCB will allow 145A to flow for about an hour without tripping. Anyone contemplating using a current which averaged over 145A for at least an hour would presumably be doing something not intended to be done in domestic premises (and would certainly need DNO permission to do whatever they were doing).
Quite - and, as I understand it, that's not what we are talking about (i.e. the reason this 'backup' 100A MCB was proposed).I agree. It would only go over 100A in some sort of fault condition.
Well, one obviously should not load a fuse beyond its 'rating' i.e. 100A in the case being discussed.What you are saying if that 95A max is on the CU do not bother?