- Joined
- 5 Nov 2019
- Messages
- 46
- Reaction score
- 1
- Country
Hi see below:can you post a close up of the boiler terminal showing what the terminal not used is please
Not ideally, because there could be a fault in the wiring between the wiring centre and the boiler, and it wouldn't test that.
If you wanted to try a test, you could check the various parts of the controls are generating the required signal. Either of the below when the system was operating properly would cause the boiler to run, by generating 230V on the boiler S/L terminal.
1) Check the orange wire in the MID POSITION VALVE terminals with the heating only on and room thermostat calling for heat, should give 230V (hot water to be set off)
2) Check the wire in terminal 1 of the CYL STAT with the hot water only on and cylinder thermostat calling for heat, should give 230V (heating to be set off)
And in both cases is the boiler S/L terminal live also?
Just done this test summary as below:
With heating on and water off orange wire isn't live only the blue one is. Switched live on boiler is also off.
Also cylinder stat is live when water is off but switched live to boiler is off in this case.
With water on and heating off cyl stat brown cable is live and switched live on boiler is also on (at 35-40v)
Any ideas?
So that's wrong. The valve isn't switching the boiler on when heating only is selected. The blue wire is neutral and should be 0V, but you have to be careful taking adhoc measurements, as the components are interconnected and stray voltages and currents can appear. Also make sure you are measuring the voltage using a genuine neutral as not all blue wires are. The mains supply N or better still the N in a local socket outlet would be best.With heating on and water off orange wire isn't live only the blue one is. Switched live on boiler is also off.
So that's as it should be and as you say the switched live is at 230V, the other end of that wire is the one I referred to below, so the boiler should have come on.With water on and heating off cyl stat brown cable is live and switched live on boiler is also on (at 35-40v)
a check for 230V on terminal strip ST2, and terminal Lr
Can you repeat the test, again, with the HW off at the programmer and cylinder thermostat and the heating on at the programmer and room thermostat. This time you are looking for 230V on the MID POSITION VALVE white wire. If there's 230V there can you check the orange wire again also. Without changing the controls from the above, can you check the manual lever underneath the motorised valve, is it loose & floppy or is there resistance when you slide it.