- Joined
- 27 Jan 2008
- Messages
- 23,698
- Reaction score
- 2,670
- Location
- Country
Only in collage and university libraries, the county library was a dead loss.
Indeed. As you might have guessed, I've got access to BSs online I don't need them for the day job , but it doesn't cost any extra for me to access them.Thank you Simon, it has been a problem since I started as an electrician, that near impossible without spending a lot of money on the books to find out myths from fact
And that includes articles where you'd expect the authors to know better As I mentioned, one article I came across was an IET Wiring Matters which you'd think ought to be "impartial" in such things.which is not helped by trade articles which are clearly designed to sell their goods not give facts.
I had almost exactly the same experience and also cancelled my subscription, at least partially for that reason (as well, as you say, rising cost).As an aside, I used to subscribe to Which? One of the factors in cancelling (apart from the rising cost) was when they'd have reports on a subject area I know a bit about - and I'd be left thinking WTF at the errors/omissions/general inaccuracies
OK, thanks. When I have some time, I'll have words with my 'local' libraries (who claim I can't do it on-line), then. I suppose it's possible (probable) that different libraries (or LAs) vary in the extent to which they offer on-line access.Yes I have had access to BSOL via my local library web portal. I had another search and have found the login page - http://www3.lancashire.gov.uk/onrl/BSI/BSiLogon.asp Just need to find my library card number now.
That seems to 'depend'. The below is the 'current' version being offered for sale by BSI. It's called BS EN 61439-3:2012, but, as you see, says it was published in March 2019 -so I guess probably includes contains Amendments. What's the 'publication date' on the version you're looking at?Found it - but the only 61439-3 is from 2012. ... Is there a newer version?
... which seems to be a bit more specific.[/QUOTE]Many thanks, Simon. Very briefly .... Indeed, but the rest of that sentence reads
[QUOTE}[a consumer unit] incorporating components and protective devices specified by the manufacturer complying with
BS EN 61439-3, including the 16kA conditional short-circuit test described in Annex ZB of the standard.
HOW MUCH Yes, without access via public libraries (or for some of us, a work subscription to the online service), it would indeed be a very expensive business getting these.The below is the 'current' version being offered for sale by BSI.
Indeed, but ...... Sorry I didn't pick up on this at the time. You are correct, the option of a Consumer Unit with 16kA devices is one option - but that specific clause explicitly allows the use of an 61439-3 board with devices rated for the prospective faults current applicable to the installation. ..
I am obviously at a considerable disadvantage by not having seen the actual Standard but, my 'understanding'(based on other things I've read) is that the "16kA conditional short-circuit test described in Annex ZB" is a test that confirms that breaking capacity of a combination of 'standard' 6kA devices and the cutout fuse (hence, perhaps, the "100A" 'requirement"?) is satisfactory. Is that not correct?So in effect, there is the choice of "use a CU (with 16kA devices) and don't worry about fault breaking capacity" or pick any board as long as you've considered the ratings.
I think you've answered your own question, at least in terms of 'spec/characteristics of the product' (i.e. if it were a "Product Standard", which most Standards are) .....But then here's a thought ... If BS 7671 says (to paraphrase) "use something to standard EN BS nnnnn", then does the electrician need to know what is in EN BS nnnnn in order to follow 7671 ? Or is it sufficient to simply take the work of the vendor who put "EN BS nnnnn" on the labels ? I suppose the answer to that is generally no - you don't need to get and read the other standard unless you plan doing something "unusual" and need to understand the nuances.
I suppose that depends upon the actual requirements of 61439-3 and, to some extent, as above, whether Annex ZB is 'Normative'. If the situation is that 61439-3 requires some 16kA test to have been passed (whether the 'conditional' test in Annex ZB or some other specified one - maybe in other Annexes?), then I suppose that compliance with the Standard is all one needs to know, and that the extra words you suggest would be unnecessary?Being a bit naughty, has anyone seen a CU described as "EN BS 61439-3 including 16kA tests to appendix ZA" ? I don't recall seeing such, but without such a statement, the person fitting it doesn't know for certain that the CU does in fact meet the requirements for that option - just having 16kA printed on the front doesn't meet the requirement since there are other tests in 61439-3 that it could refer to
No, it's informative.Indeed, but ...
I suppose a fairly crucial question is whether or not Annex ZB is 'Normative'. Is it?
I think that is the crucial bit. In my attempts to understand this, I've read some pretty complicated theory and maths about 'breaking capacity' when there is a combination of a fuse and MCB in series.Where the devices are not rated for 16kA fault current, then there's further tests to be done, including on an outgoing device of minimum current rating. The test rig does include a BS88-3 100A fuse, or a BS1361 type II fuse. The purpose is stated as being : The following test procedure is intended to verify the performance of the incoming device and its connections, and any other item in the CDB not separately rated in excess of 16 kA, when the complete CDB is protected by a fuse-link complying with BS 88.3 (formerly BS 1361). This type test shall be deemed to cover the use of any other short-circuit protective device having a Joule integral (I2t) and cut-off current not exceeding values given in item b) below, at the rated voltage, prospective current and power factor.
So as the old saying goes, every day is a learning day. I hadn't really picked up on the "combination including 100A fuse" bit.
Indeed. As you will have seen, I've often asked this question myself. Although my experience is pretty limited, I've personally never seen a PFC appreciably above 1kA, let alone 6kA - but whenever I ask the question, I am assured that some extremely low Zes do exist, at least in London. As you imply, I would have thought that, in most cases, the cable from the street to the cutout would often be enough, on its own, to get the PFC down to 6 kA or less.But I am curious, does anyone ever find a prospective fault current ever approaching 6kA, let alone exceeding it in the real world ? I figure you'd almost need a large cross-section connection to the substation in your basement to get it. You'd need a Ze below 0.04Ω to get 6kA, if the distribution cable was (say) 35mm² in the street then that's only 30m needed assuming a zero impedance supply at the substation. You still only need 61m of 70mm². Our service cable (i.e. just from our cut out to the street cable) at home probably provides half the required impedance on it's own.
I continue to be fairly amazed. Even if the TN-S sheath had only the same impedance as the L conductor (which I rather doubt), that would presumably require at least 50mm² cable all the way from the substation to your installation. I must say that I had always assumed that the 'extraordinarly high' PFCs we hear about would/could only ever be seen with TN-C-S.Measured Ze of 0.1 Ohms here in SW London. TN-S system about 100m from 11kV substation.
