Reckon this might be the least worst option.
https://www.ebay.co.uk/itm/SK-623-5...-/193743506350?_trksid=p2349624.m46890.l49292
Why not make it simple?
Add a relay to open a motorised valve, so the heat is piped into another part of your system?
Thing is, as you may know, the motorised valve when open calls the boiler to come on. So it’s not that straightforward. Not impossible but not “simple”
You said you had a fancy relay system, it cannot be that difficult to interrupt the feed from valve to boiler, to inhibit the boiler seeing a demand when the valve is opened.
lol - my wife said that to me earlier today. I think she’s either a genius or has a part time job as a plumber![]()
she is probably a member of the secret womens website where they discuss such things. It is disguised as a baby care website to keep plumbers away.
maybe you’re right, but I always thought the idea was to bring down the temp slowly of the exchanger and then switch off when temp is lowered
my post was also to elicit replies like yours, questioning the premise of what I’m trying to do. Because yeah, maybe I don’t quite get the point of overrun
What happens to the water temperature whilst the pump overrun is running? Why do you believe what is happening is insufficient?
My boiler (Vaillant 438) had approximately 3m of pipe between flow/return through an ABV (had, as I now have a LLH, but the pipe run is still relatively short). The idea was to keep the water circulating and allowing it to slowly cool down. Even on such a short run, the temperature drop would be quite dramatic initially.
Stress on the hex is caused by the delta T of flow and return being too high. In the pump overrun scenario, the flow and return temps are roughly the same.
Maybe I've got it all wrong - but sounds like you're trying to solve a problem which doesnt exist.
and when the overrun comes on it can increase to say 90 or 91 in the first minute or two and then it comes down slowly to say 81 and then say 76 after 3-5 minutes
Two things I’ll try:
- Extend relay timer so overrun runs for longer. Won’t reduce rate of heat loss but will leave temp lower ultimately
- I have a small unused rad I could hook in as a “heat sink” (this won’t be done for a while, but would work better)
You are overthinking the need for it. All you need to aim for, is removal of the residual heat in the heat exchanger - to get it's temperature down to that of the rest of the system and prevent the sudden removal of the cooling flow of water, allowing the temperature in the heat exchanger rising. You can do that by running the pump for a few minutes with a valve open, to distribute the heat.
Can't you just wire the pump and heating valve in parallel?