I should have said that your boiler does expect a flow/return differential of up to 20C. The higher the differential, the lower the flow so the smalller the pressure loss. In which case the bypass may not need adjusting. Correctly balancing for a higher differential should solve your problem.
What procedure did you follow when balancing the system?
What is the total kW (at 50dt) of your radiators?
Do you know the actual heat loss of your house?